220 or 240 Volrs AC
Sorry, there was a problem. Please try again later.The LG - 36" Built-In Electric Cooktop - Black, Model # LCE3610SB can consume up to 9200W at 240 VAC and a 50 Amp circuit breaker with a wire gauge #8 AWG must be used. A 3-wire or 4-wire single-phase 120/240 or 120/208 volt, 60 Hz AC-only electrical supply is required on a separate circuit fused on both sides of the line (time-delay fuse or circuit breaker is recommended). DO NOT fuse neutral. The fuse size must not exceed the circuit rating of the appliance specified on the nameplate. You will need to install a junction box under the cabinet and run 120/240 or 120/208 volt, AC wire from the main circuit panel. The appliance should be connected to the fused disconnect (or circuit breaker) box through flexible armored or nonmetallic sheathed cable. The flexible armored cable extending from this appliance should be connected directly to the grounded junction box...^IFV