1-5 of 5 Answers
Highly unlikely. A typical sump pump is 1/3 HP. This converts to about 250 VA. When an induction motor starts it typically draws 5 times rated current or in this case about 1250 VA or about 3 times the rating of this UPS.
Sorry, there was a problem. Please try again later.Thank you for your inquiry. Unfortunately we don't recommend using our BackUPS units with a motorized load. One potential issue is the inrush current draw for a motor can easily overload a BackUPS unit. BackUPS are ideal for computer equipment and may result in the erratic behavior when connected to a motor. To protect this type of equipment, APC recommends first determining the appropriate size UPS for the motor load in question and ensure the UPS is large enough to handle the start-up inrush current draw of the motor. Secondly, select a UPS which outputs a pure sine wave when on battery, such as a Smart-UPS.
Sorry, there was a problem. Please try again later.Check the watts on the pump and compare it to the stats on the specs re time at that draw. Clearly, it should not be in a damp place.
Sorry, there was a problem. Please try again later.You could but it will not last very long. Sump pumps usually pull a lot of power. I would buy a bigger backup. Hope that helps.
Sorry, there was a problem. Please try again later.Yes,as long as it is 110. The currant draw of the pump will determine how long the APC will run the pump in the event of a power outage.
Sorry, there was a problem. Please try again later.