1-3 of 3 Answers
I have not seen an F02 error on my unit but I did charge it before I connected anything to it. You also need to plug in the battery. The battery is in the unit but not connected. I looked up the error and the APC troubleshooting guide says: F02 = On-Battery Output Short Troubleshooting Procedure:: Turn the Back-UPS off. Disconnect all equipment from the Battery Backup outlets and the turn Back-UPS on. Re-connect equipment one item at a time. If the output is tripped again, disconnect the device that caused the error. I hope this helps.
Sorry, there was a problem. Please try again later.Thank you for your interest in our products. If the info that the previous poster mentioned doesn't clear up the issue please reach out to an APCbySchneider for further assistance. We offer email and chat services through our support site. For the fastest service visit our chat at https://www.apc.com/us/en/tools/chat/.
Sorry, there was a problem. Please try again later.Never plug a printer into a UPS, The excessive power draw will damage it.